We just had a new furnace and central air installed in our 1996 Redman and the air condioner is VERY loud, is this normal?

Happyhome82
Posts: 1
Joined: Sat Jan 20, 2024 1:27 pm

Re: CentrAL AIR 96 REDMAN

Post by Happyhome82 » Sat Jan 20, 2024 1:31 pm

If the new appliance is louder than the old system here is a ferw things to check.

1. Did they oversize the new appliance? Often time the ducts can not handle the higher cfm of a new appliance.
2. Is the cabinet sealed? Sometimes the installers can forget to seal all of the opening s and the unit can whistle.
3. Its very possible the blower motor wheel is out of balance which can cause horrible noise.

I purchased my new system from https://myhvacprice.com and the local company got me a retrofit with an Inertherm I think it was called.